Lightbulb { boiler and turbine } control modes


Boiler Master (Firing Rate Demand)


Boiler Master (basic firing rate demand) computation is dependent on the Current operating mode like

Coordinated mode,
Boiler Follow mode,
Turbine Follow mode,
Manual mode.

This demand is transmitted in parallel to the fuel and air control sub -loops.



(1) Unit Startup

During the unit startup, Boiler Master is determined as a fixed demand with the rate to obtain the optimum boiler steam temperature rising and steam flow until HP turbine bypass control valve is fully closed. This demand will be adjusted manually or automatically according to the unit startup mode.

During this period, Main steam pressure is controlled by HP turbine bypass control valve. During the unit start up, the operating mode will be Manual Mode both Turbine governor and Boiler Master manual.





(2) Normal operation

After HP turbine bypass control valve is fully closed, the operating mode will be normally transferred to Coordinated Control Mode.

In case of Coordinated Control Mode, the turbine governor controls MW and Boiler Master controls the main steam pressure.

In case of Boiler Follow Mode, Boiler Master also controls the main steam pressure.

In case of Boiler Master Manual or load runback, the operating mode becomes Turbine Follow Mode and turbine governor controls the main steam pressure.





Attached Images
File Type: jpg HPTV.JPG (57.8 KB, 8 views)
__________________
http://science-hamza.blogspot.com
Reply With Quote
  #2 (permalink)  
Old 01-07-2011
PPF Member
Power Rookie
 
Join Date: Oct 2010
Posts: 8
Rep Power: 44
blackblaze is on a distinguished road
Question

Quote:
Originally Posted by khaled hamza View Post

Boiler Master (Firing Rate Demand)


Boiler Master (basic firing rate demand) computation is dependent on the Current operating mode like

Coordinated mode,
Boiler Follow mode,
Turbine Follow mode,
Manual mode.

This demand is transmitted in parallel to the fuel and air control sub -loops.



(1) Unit Startup

During the unit startup, Boiler Master is determined as a fixed demand with the rate to obtain the optimum boiler steam temperature rising and steam flow until HP turbine bypass control valve is fully closed. This demand will be adjusted manually or automatically according to the unit startup mode.

During this period, Main steam pressure is controlled by HP turbine bypass control valve. During the unit start up, the operating mode will be Manual Mode both Turbine governor and Boiler Master manual.





(2) Normal operation

After HP turbine bypass control valve is fully closed, the operating mode will be normally transferred to Coordinated Control Mode.

In case of Coordinated Control Mode, the turbine governor controls MW and Boiler Master controls the main steam pressure.

In case of Boiler Follow Mode, Boiler Master also controls the main steam pressure.

In case of Boiler Master Manual or load runback, the operating mode becomes Turbine Follow Mode and turbine governor controls the main steam pressure.





What is the typically heat rate and efficiency for this setup?
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 02:33 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0