Lightbulb Over Frquency happened at a windy winter night


Over Frquency happened at a windy winter night





at 3:00 am , A sudden frequency fluctuation happened , that cause the MW output fluctuate with the grid frequency , Unit 7 was at Coordinated Mode ( Boiler Master – Auto , Turbine Set – Auto ) , The load fluctuated accordingly to the frequency from 105 MW to 90 MW, and increased to 105 MW.
After a little time, frequency reached 50.1 HZ – therefore the MW output reached 20 MW,
Also, Boiler Master responds by reducing Air Flow and Fuel Gas Flow for the boiler. The load still decreased until it reached 2 MW, and to (-2 MW), without coming the signal of Reverse Power.


At this instant we trip the turbine manually.
We wanted to conserve the boiler to be in service, but HP-TBV opens widely within 30 sec., and sucking all drum level to +267 mm, resulting MFT Protection to the boiler.


The first out indication of MFT at BMS was (Drum level HH). “


There were a lot of discussion and arguments about what is the cause of this accidents , and what should operators do ?

I attached A chart Table shows the different parameters changed at each same time !! , If any one has an opinion about what happened , plz tell me !!

Attached Files
File Type: txt links.txt (168 Bytes, 5 views)
__________________
http://science-hamza.blogspot.com
Reply With Quote
  #2 (permalink)  
Old 12-17-2010
PPF Member
Power Rookie
 
Join Date: Dec 2010
Location: Egypt
Posts: 40
Rep Power: 56
khaled hamza is on a distinguished road
Lightbulb

After I discussed what happened the outage three days ago - the situation I posted previously - I found an explanation for that: -

In winter days , Electrical loads are decreasing here in Egypt especially at night , therefore the frequency increases from 50 HZ .
the Dispatch should decrease the loads of the generating units to limit the decrease of frequency , and the generating unit's Operator should take care of such these situations.

At that night , Turbine's operator should realize the increase of frequency and the decrease the actual MW , he should switch the turbine control to manual , to limit the decrease of MW , Then he should switch the HPTV to manual and start open it gradually to release the over pressurized steam at HPTV .

The Boiler's operator should maintain the main steam pressure to the actual MW by the percentage opening of HPTV , therefore the boiler master in that situation will control main steam pressure tracking to the opening of HPTV , then he should try to limit the load as possible away from Fluctuations .

After frequency is settled we can increase the MW and close the HPTV , then switch again the Turbine set and Boiler Master to Automatic Mode.

That is a brief conclusion for what should happened in such that situation.
__________________
http://science-hamza.blogspot.com
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 02:18 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0