Setting of Reverse Power Relays Data for setting calculations -Rated Capacity of Generator -------- 440,000 KVA -No Load Loss of Generator --------- 1,785 KW -No Load Loss of Turbine ---------- 1,350 KW -No Load Loss of TG unit ---------- 3,135 KW -Permissible Motoring Time ------- 60 Sec. -Relay Constant ------------------- 1 P.U. = Generator KVA Setting Of Reveres Power Relay 32G ( #1 ) 1- Reverse Power Trip Level Trip Level < No load loss of TG unit * 0.3 = 3,135 * 0.3 = 940.5 KW Pick up = Trip level / relay constant = 941 / 440,000 = 0.0021 P.U. Setting = - 0.002 P.U. ( 880KW ) 2- Reverse Power Trip Delay Trip Delay < Perm. Motoring time (60 Sec.) Setting = 50 Cycles (1 Sec.) Setting Of Reveres Power Relay 32G ( #2 ) 1- Reverse Power Trip Level Trip Level < No load loss of TG unit * 0.5 = 3,135 * 0.5 = 1,568 KW Pick up = Trip level / relay constant = 1,568 / 440,000 = 0.004 P.U. Setting = - 0.004 P.U. ( 1,760KW ) 2- Reverse Power Trip Delay Trip Delay < Perm. Motoring time (60 Sec.) Setting = 750 Cycles (15 Sec.)
__________________
http://science-hamza.blogspot.com
Last edited by khaled hamza; 12-19-2010 at 08:25 AM. |
|
|||
|
Maybe Dynasty was saying that a soft open is +3mw and a rolling the lockout from the gen protection is at -3mw.
|
![]() |