Default Reverse Power Relay Settings

What is the typical reverse power relay setting to trip open the generator breaker?
Reply With Quote
  #2 (permalink)  
Old 10-17-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 26
Rep Power: 81
dynasty is on a distinguished road
Default RE: Reverse Power Relay Settings

Our GTs opens 52G at +3MW to avoid motoring the generator. The relays trip the gen breaker at -3MW.
Reply With Quote
  #3 (permalink)  
Old 11-03-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 14
Rep Power: 76
highvoltage is on a distinguished road
Default RE: Reverse Power Relay Settings

We open the the generator breaker upon reverse power of -1.5MW
Reply With Quote
  #4 (permalink)  
Old 12-08-2008
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 2
Rep Power: 69
bsc1978 is on a distinguished road
Default RE: Reverse Power Relay Settings

normally it is set at 5-7% of machine rating
Reply With Quote
  #5 (permalink)  
Old 10-11-2009
PPF Member
Power Rookie
 
Join Date: Oct 2009
Location: Missouri
Posts: 9
Rep Power: 61
buntin is on a distinguished road
Default I' m confused.

Quote:
Originally Posted by dynasty View Post
Our GTs opens 52G at +3MW to avoid motoring the generator. The relays trip the gen breaker at -3MW.
You say "52G opens at +3mw to avoid motoring". Then you say "relays trip the gen breaker at -3mw"?

Your answer makes no sense.
Reply With Quote
  #6 (permalink)  
Old 12-19-2010
PPF Member
Power Rookie
 
Join Date: Dec 2010
Location: Egypt
Posts: 40
Rep Power: 48
khaled hamza is on a distinguished road
Lightbulb



Setting of Reverse Power Relays

Data for setting calculations
-Rated Capacity of Generator -------- 440,000 KVA
-No Load Loss of Generator --------- 1,785 KW
-No Load Loss of Turbine ---------- 1,350 KW
-No Load Loss of TG unit ---------- 3,135 KW
-Permissible Motoring Time ------- 60 Sec.
-Relay Constant ------------------- 1 P.U. = Generator KVA



Setting Of Reveres Power Relay 32G ( #1 )

1- Reverse Power Trip Level

Trip Level < No load loss of TG unit * 0.3
= 3,135 * 0.3
= 940.5 KW
Pick up = Trip level / relay constant
= 941 / 440,000
= 0.0021 P.U.
Setting = - 0.002 P.U. ( 880KW )

2- Reverse Power Trip Delay

Trip Delay < Perm. Motoring time (60 Sec.)
Setting = 50 Cycles (1 Sec.)






Setting Of Reveres Power Relay 32G ( #2 )

1- Reverse Power Trip Level

Trip Level < No load loss of TG unit * 0.5
= 3,135 * 0.5
= 1,568 KW
Pick up = Trip level / relay constant
= 1,568 / 440,000
= 0.004 P.U.
Setting = - 0.004 P.U. ( 1,760KW )

2- Reverse Power Trip Delay

Trip Delay < Perm. Motoring time (60 Sec.)
Setting = 750 Cycles (15 Sec.)
__________________
http://science-hamza.blogspot.com

Last edited by khaled hamza; 12-19-2010 at 08:25 AM.
Reply With Quote
  #7 (permalink)  
Old 12-20-2010
PPF Member
Power Rookie
 
Join Date: Oct 2010
Posts: 6
Rep Power: 36
briandallas is on a distinguished road
Default

Quote:
Originally Posted by buntin View Post
You say "52G opens at +3mw to avoid motoring". Then you say "relays trip the gen breaker at -3mw"?

Your answer makes no sense.
Maybe Dynasty was saying that a soft open is +3mw and a rolling the lockout from the gen protection is at -3mw.
Reply With Quote
  #8 (permalink)  
Old 07-31-2011
PPF Member
New Person
 
Join Date: Jul 2011
Posts: 1
Rep Power: 0
d2dprajesh is on a distinguished road
Default

Our 126MW Frame 9E GE machine has
-2.5MW at 0.5 sec. delay.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 11:19 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0