Lightbulb Generator Stator Earth Fault Relay (64G) - 27TN.

Generator Stator Earth Fault Relay (64G) - 27TN.

-For high impedance grounded generators, a voltage relay across the secondary winding of the generator neutral grounding transformer is used to detect the ground fault on the generator stator winding.

-The neutral over voltage function (59N) responds to the fundamental frequency voltage at the generator neutral that appears when a ground fault occurs.

-Normally, it will protect up to 90≈ 95 % of the stator windings.

-The neutral under voltage functions responds to 3rd harmonic voltage measured at the generator neutral. When used in conjunction with the neutral over voltage function, it provides 100% ground fault protection of the stator winding.

-In healthy state, the machine 3rd harmonic voltage is distributed over the windings such that the maximum occur at the star point neutral and at the line terminal. For a ground fault close to the neutral, all the 3rd harmonic voltage is transferred to the line terminals. Consequently, the relay function will see a 3rd harmonic under voltage at the neutral end and will operate the protection element.
Attached Images
File Type: jpg gen_1.JPG (55.7 KB, 3 views)
File Type: jpg stator_earth.JPG (7.2 KB, 3 views)
__________________
http://science-hamza.blogspot.com
Reply With Quote
  #2 (permalink)  
Old 12-29-2010
PPF Member
Power Rookie
 
Join Date: Oct 2010
Posts: 8
Rep Power: 44
blackblaze is on a distinguished road
Exclamation ground earth fault

Hello, can you explain how the generator neutral ground fault works with an LCI (static start) system attached to the generator stator for motoring at startup?
thanks



Quote:
Originally Posted by khaled hamza View Post
Generator Stator Earth Fault Relay (64G) - 27TN.

-For high impedance grounded generators, a voltage relay across the secondary winding of the generator neutral grounding transformer is used to detect the ground fault on the generator stator winding.

-The neutral over voltage function (59N) responds to the fundamental frequency voltage at the generator neutral that appears when a ground fault occurs.

-Normally, it will protect up to 90≈ 95 % of the stator windings.

-The neutral under voltage functions responds to 3rd harmonic voltage measured at the generator neutral. When used in conjunction with the neutral over voltage function, it provides 100% ground fault protection of the stator winding.

-In healthy state, the machine 3rd harmonic voltage is distributed over the windings such that the maximum occur at the star point neutral and at the line terminal. For a ground fault close to the neutral, all the 3rd harmonic voltage is transferred to the line terminals. Consequently, the relay function will see a 3rd harmonic under voltage at the neutral end and will operate the protection element.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 02:17 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0