Lightbulb Reverse Power Protection., Theory & Setting .

Reverse Power Protection.


1- Protection against overspend 32G (# 1).

In case of Turbine Failure, the Turbine is tripped and then the Generator is tripped by operation of reverse power relay to prevent overspending of the Turbine generator unit.

2- Protection against generator motoring 32G (#2).

-Generator motoring protection is designed for the prime mover or the system, rather than for the generator.

- With steam turbines, Turbines will overheat on low steam flow, motoring results from a low input To the Ac Generator,

- When This I/P can’t meet all the losses, the deficiency is supplied by absorbing real power from the system.

- since field excitation should remain the same , the same reactive power would flow as before motoring , thus, on motoring the real power will be into the generator, while the reactive power may be either flowing out or into the generator






Setting of Reverse Power Relays

Data for setting calculations
-Rated Capacity of Generator -------- 440,000 KVA
-No Load Loss of Generator --------- 1,785 KW
-No Load Loss of Turbine ---------- 1,350 KW
-No Load Loss of TG unit ---------- 3,135 KW
-Permissible Motoring Time ------- 60 Sec.
-Relay Constant ------------------- 1 P.U. = Generator KVA



Setting Of Reveres Power Relay 32G ( #1 )

1- Reverse Power Trip Level

Trip Level < No load loss of TG unit * 0.3
= 3,135 * 0.3
= 940.5 KW
Pick up = Trip level / relay constant
= 941 / 440,000
= 0.0021 P.U.
Setting = - 0.002 P.U. ( 880KW )

2- Reverse Power Trip Delay

Trip Delay < Perm. Motoring time (60 Sec.)
Setting = 50 Cycles (1 Sec.)






Setting Of Reveres Power Relay 32G ( #2 )

1- Reverse Power Trip Level

Trip Level < No load loss of TG unit * 0.5
= 3,135 * 0.5
= 1,568 KW
Pick up = Trip level / relay constant
= 1,568 / 440,000
= 0.004 P.U.
Setting = - 0.004 P.U. ( 1,760KW )

2- Reverse Power Trip Delay

Trip Delay < Perm. Motoring time (60 Sec.)
Setting = 750 Cycles (15 Sec.)




Attached Images
File Type: jpg gene..jpg (86.0 KB, 3 views)
File Type: jpg reverse.JPG (7.7 KB, 2 views)
__________________
http://science-hamza.blogspot.com

Last edited by khaled hamza; 12-19-2010 at 07:28 AM.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 02:17 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0