Default Moisture in pressure sensing line

We are witnessing moisture in a pressure sensing line which is constantly damaging the diaphragm and internal components of the pressure transmitter. The pressure is monitoring exhaust pressure of roughly 8inH20 and 1300 degs F. We would see pressure perturbations before the transmitter fails. We have tried installing drip legs, increasing slope and to no avail. Any recommendations? thanks
Reply With Quote
  #2 (permalink)  
Old 07-06-2008
PPF Member
Power Rookie
 
Join Date: May 2009
Posts: 31
Rep Power: 83
TECHguy is on a distinguished road
Default RE: Moisture in pressure sensing line

have you tried insulating the lines? The delta T is causing condensation to form. By insulating the lines you will be reducing the amount of temp change. Also you can consider reducing the length of the sensing lines. I think Rosemount makes capillaries where the diaphragm is mounted separately from the signal conditioner.
Reply With Quote
  #3 (permalink)  
Old 08-05-2008
PPF Member
Power Regular
 
Join Date: Apr 2009
Posts: 54
Rep Power: 95
RStevens is on a distinguished road
Default RE: Moisture in pressure sensing line

increase the slope of the tubine so the moisture runs out. also you can blow down the lines regularly to remove the moisture...best bet is to insulate the lines to avoid the change in temp which is causing the moisture. We have the rosemount capillary transmitters on site with great success. I dont know if the thought process behind using them is to avoid moisture in the sensing lines but we have no moisture issues with them.
Reply With Quote
  #4 (permalink)  
Old 03-07-2011
PPF Member
New Person
 
Join Date: Mar 2011
Posts: 2
Rep Power: 24
AnkurSood is on a distinguished road
Smile Install purge rotameter

Quote:
Originally Posted by powerguru View Post
We are witnessing moisture in a pressure sensing line which is constantly damaging the diaphragm and internal components of the pressure transmitter. The pressure is monitoring exhaust pressure of roughly 8inH20 and 1300 degs F. We would see pressure perturbations before the transmitter fails. We have tried installing drip legs, increasing slope and to no avail. Any recommendations? thanks
Hi,
We were facing similar problem in our utility boiler furnace Pressure trabsmitter.
There the pressure is 4-6 INH2O and the temp is around 400-500 Deg C.
We installed a purge rotameter in the impulse line.After that the moisture problem has been resolved.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Discussion Replies Last Post
sliding pressure vs constant pressure mode Mikas Steam Powered Turbines 6 08-27-2010 03:20 PM

Subscribe to Power Plant Forum

All times are GMT -4. The time now is 11:51 AM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0