Default Changing out brushes and how often?

We have a GE 7H2 generator and have been changing out brushes every 6 months during our seasonal outages. The electricians does not feel comfortable changing brushes online and are a baseload unit. Is your site brave enough to change brushes out online or do you wait for a shutdown? Also what is the frequency? We run at high lagging MVARS, near the OEL limit which really shortens the life of the brushes.
Reply With Quote
  #2 (permalink)  
Old 11-27-2008
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 5
Rep Power: 33
Lar944 is on a distinguished road
Default RE: Changing out brushes and how often?

These brushes were designed to be replaced online. There is a clear indicator that the spring is no longer seating the brush, replace prior to this on a daily basis whenever noted.
Reply With Quote
  #3 (permalink)  
Old 11-27-2008
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 5
Rep Power: 33
Lar944 is on a distinguished road
Default RE: Changing out brushes and how often?

Also brush changes should be an operation dept task, incorporated into daily rounds.
Reply With Quote
  #4 (permalink)  
Old 12-13-2008
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 4
Rep Power: 33
mbarazeen is on a distinguished road
Default RE: Changing out brushes and how often?

we have the same Model and doing online ofcause. nearly the same frequency ofr every brushes, but some are even faster. we have replaced old model brushes that are with plastic roller by new design, since they easily hang up when over heated. still the new design give some problems, specially over heating of prussure springs that leads less performance and dis engage the brush from operation/ hang up.

atleast once in every month we open the comparment cover for online maintenance, operation routine check it visually every day each shift, since its so critical and recently we have a bad experience of flash over in another plant of us. changing brushes online is practical and require more experience to feel comfortable. during shutdown a good maintenance is possible.

razeen
KSA
Reply With Quote
  #5 (permalink)  
Old 01-28-2009
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 1
Rep Power: 0
bowhuntinelk is on a distinguished road
Default RE: Changing out brushes and how often?

There have been some explosion issues with carbon dust buildup in the compartment as well. While changing brushes on line is pretty standard, I would clean the compartment of dust at least annually to prevent this.
Reply With Quote
  #6 (permalink)  
Old 02-27-2009
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 26
Rep Power: 44
dynasty is on a distinguished road
Default RE: Changing out brushes and how often?

another question to add, how often do you change the shaft grounding brush? does anyone even inspect it on a regular basis?
Reply With Quote
  #7 (permalink)  
Old 09-14-2009
PPF Member
New Person
 
Join Date: Aug 2009
Posts: 3
Rep Power: 24
neger is on a distinguished road
Default

Hi

we inspect the grounding and excitation brushes once weekly, we change it according to its thickness, and we change the excitation brushes at base load (up to 250 MW) but with one brush at time, if we removed two brushes at the same time the generator will trip.

siemens generator (50 Hz - 16.5 KV)
Excitation voltage = 255 VDC

Last edited by neger; 09-14-2009 at 12:45 PM.
Reply With Quote
  #8 (permalink)  
Old 10-26-2009
PPF Member
New Person
 
Join Date: Apr 2009
Posts: 4
Rep Power: 33
mbarazeen is on a distinguished road
Default changing grounding brushes

we normally go for inspection for grounding brushes every 3 months during offline water wash shutdown, further more if there will be any alarm for shaft voltage, its attended imediately. some times only cleaning of the shaft by cleaner spray after removal of brushes when rotating also has given good results.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On



All times are GMT -4. The time now is 02:30 AM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0