Default Query about Frame 9E Gas Turbine with Mark IV Control

On frame 9E Gas Turbines(Mark IV), if additve dosing panel trips or additive flow rate becomes nil while m/c is running on furnace oil(Our GTs always run at base load) then it converts to HSD on auto & also takes shutdown command. Now if m/c is not restarted with in two minutes then boiler(HRSG) trips (while GT is running in combined cycle mode).

Now as far as Siemens V94.2 Gas turbines are concerned, if dosing panel trips while GT is running on LSFO then it only converts to HSD on auto i.e. no shutdown command.

Actually in case of GE Frame9E turbines, When additive dosing panel trips or additive dosing stops for some reason. A relay picks up because of no flow rate of additive & initiates a signal to heavy fuel permissive check relay because of which fuel changeover command to HSD is initiated. Now same signal of no additive flow rate also goes to turbine normal shutdown relay. In addition to this signal, turbine normal shutdown relay also takes into account a signal about position of fuel changeover valve (pneumatic operated). If position of this valve is not towards HSD within 10 seconds of initiation of additive no flow rate signal then turbine will take shut down command. Fuel changeover valve takes about 20 to 25 seconds to change its position from furnace oil to HSD. So, if we increase delay in turbine shutdown command signal from 10 to 30 seconds then with in this time of 30 seconds changeover valve would change its position towards HSD & hence there will be no shutdown signal (as conditions for shutdown would not meet because of changeover valve position would be towards HSD). Result would be that turbine will be running on furnace oil at base load for 20 seconds without dozing. Is that too much??

Kindly advise me whether this modification should be made or not. Has anyone performed this kind of modification on his GT (Frame9E with MarkIV control)?
We will certainly ask OEM before any such modification but I just want to know your opinion on that.
Reply With Quote
  #2 (permalink)  
Old 09-12-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 36
Rep Power: 49
RStevens is on a distinguished road
Default RE: Query about Frame 9E Gas Turbine with Mark IV Control

What was GEs response? you looking to upgrade your MKIV to something more modern such as the MKVIe?
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Discussion Replies Last Post
Lm2500 gas turbine users topic block1 Aero derivative Turbines 5 09-04-2008 08:23 AM
cost and performance: steam turbine or gas turbine? kidillusion Steam Powered Turbines 1 07-02-2008 05:14 PM


All times are GMT -4. The time now is 02:25 AM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2010, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0