Question Gas turbine Frame 6

We are operating GE Frame 6 Gas turbine ( Gas only) . We had gas turbine ventillation duct gas detection in 2 sensers. We inhibited and checked for LEL & Methane . Report was negative. Later we identified cross fire outer tube gasket leak.
GT was shut down, gasket replaced, gas senser replaced, its cable checked. After restarting after 4 hours again gas senser detected gas . Lab analysis reports negative. But 6 of the cross fire outer tube flange leak was observed. GT is running with sensers inhibited.
Thermal imaging indicates 15 deg C increase in the crossfire outer tube .

Can someone share any similar experience/ guide this situation.
Reply With Quote
  #2 (permalink)  
Old 05-25-2010
PPF Member
Power Regular
 
Join Date: Apr 2009
Posts: 54
Rep Power: 95
RStevens is on a distinguished road
Lightbulb Crossfire tube leaks and high LEL

From my experience typically outer crossfire tube leaking does not contain methane gas since the air blowing out is from the hot CDC (combustion discharge). Hot air is discharged and pulled up to the vacuum blowers thats extracting hot air out of the compartment. Since most Haz gas sensors can only handel about 250degs F of heat before degradation, they are typically the first tell tail that you have hot air leaking our of the unit.
I've seen sporadic false LEL's which resulted in a sensor failure due to hot air leaking out of the crossfire tubing. Since the packing is normally replaced during an outage when the combustion hardware is removed, replacing it insitsu is difficult and requires splitting the packing ring. Once there is an air gap in the packing rings even the slightest hot air leakage will accelerate its failure and blow it out. I would recommend upgrading to crossfire bellows modification which uses a flexitallic gasket and expansion bellows as opposed to a graphite packing type with clearance gaps. If you have high LEL, and it is determined true, there is more than likely leaks on the gas flex lines and associated flanges. best bet for detecting leaks is your typical rag on a stick.. Good luck!

Rob



Quote:
Originally Posted by aksunil View Post
We are operating GE Frame 6 Gas turbine ( Gas only) . We had gas turbine ventillation duct gas detection in 2 sensers. We inhibited and checked for LEL & Methane . Report was negative. Later we identified cross fire outer tube gasket leak.
GT was shut down, gasket replaced, gas senser replaced, its cable checked. After restarting after 4 hours again gas senser detected gas . Lab analysis reports negative. But 6 of the cross fire outer tube flange leak was observed. GT is running with sensers inhibited.
Thermal imaging indicates 15 deg C increase in the crossfire outer tube .

Can someone share any similar experience/ guide this situation.
Reply With Quote
  #3 (permalink)  
Old 05-25-2010
PPF Member
New Person
 
Join Date: May 2010
Posts: 4
Rep Power: 45
aksunil is on a distinguished road
Default Gas turbine Frame 6 cross fire tube

Thank you Mr Stevens for an intelligent technical diagnosis and a prompt reply.

We were also thinking in the same line. We had adopted many methodology to identify the leak or any after combustion. We had used the explosive meter, we had analysed the GT turbine compartment air at defferent locaton with gas chromatograph, we had used thermal imaging and also pyrometer to identify varying range of gas and temperatures. In none of the methods we could find even traces of gas or oxydation tendency.
Based on these we had deciding to run the machine till M.I which is due in september 2010
Reply With Quote
  #4 (permalink)  
Old 05-30-2010
PPF Member
Power Rookie
 
Join Date: Jun 2009
Location: US
Posts: 13
Rep Power: 71
PowerBoy is on a distinguished road
Default Crossfire tube leaks and high LEL

Quote:
Originally Posted by aksunil View Post
Thank you Mr Stevens for an intelligent technical diagnosis and a prompt reply.

We were also thinking in the same line. We had adopted many methodology to identify the leak or any after combustion. We had used the explosive meter, we had analysed the GT turbine compartment air at defferent locaton with gas chromatograph, we had used thermal imaging and also pyrometer to identify varying range of gas and temperatures. In none of the methods we could find even traces of gas or oxydation tendency.
Based on these we had deciding to run the machine till M.I which is due in september 2010

We had similar experinces and upon further study it turned out that the leaks sufraced after water washes. Apparently water wash effulent would make its way from the CDC to the outer crossfire packing rings and the graphite would get wet. Upon startup the hot air would just blow them out. Be careful with pushing too much water into your unit which could flood the drains and water will make it way up the CDC and out towards the FWD combustion can areas. Watch out for those extra rinses and not fully opening all WW drains. thanks
__________________
O&M Manager-BSME, MSME, P.E.
Reply With Quote
  #5 (permalink)  
Old 10-06-2010
PPF Member
New Person
 
Join Date: Oct 2010
Posts: 3
Rep Power: 34
csenergy86 is on a distinguished road
Default

We currenly have a worseneing cross-fire tube leak on a Fr6B. We have known of leak for last two months only (suspect developing over last year if connected to high compartment temps). Unsure if during last offline water wash if it tripped on hi spread or other. It would have been back mid 2009.

Hoing to hold out until next month.

aksunhil, what did you find in your Sept MI?

Last edited by csenergy86; 10-06-2010 at 10:40 PM.
Reply With Quote
  #6 (permalink)  
Old 10-11-2010
PPF Member
Power Regular
 
Join Date: Apr 2009
Posts: 54
Rep Power: 95
RStevens is on a distinguished road
Exclamation

Quote:
Originally Posted by csenergy86 View Post
We currenly have a worseneing cross-fire tube leak on a Fr6B. We have known of leak for last two months only (suspect developing over last year if connected to high compartment temps). Unsure if during last offline water wash if it tripped on hi spread or other. It would have been back mid 2009.

Hoing to hold out until next month.

aksunhil, what did you find in your Sept MI?

Sounds like you need to upgrade to the Crossfire Bellows mod which uses spiral wound gaskets instead of those crappy graphite rope/packing.
Reply With Quote
  #7 (permalink)  
Old 10-11-2010
PPF Member
New Person
 
Join Date: Oct 2010
Posts: 3
Rep Power: 34
csenergy86 is on a distinguished road
Default

Are the crossfire bellows available for frame 6 MS6001B machines? I wa under the impression it was only for F-technology machines.
Reply With Quote
  #8 (permalink)  
Old 10-13-2010
PPF Member
New Person
 
Join Date: Oct 2010
Posts: 4
Rep Power: 35
rccraft is on a distinguished road
Lightbulb GE combustion turbine

Quote:
Originally Posted by csenergy86 View Post
Are the crossfire bellows available for frame 6 MS6001B machines? I wa under the impression it was only for F-technology machines.
good question. We have 7Fa and 6B's on site and will ask our GE sales rep to see if the bellows are available on the 6B.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 11:47 AM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0