Default DHCP H2 analyzers purity decay issue

We have E-ONEs dual hydrogen analyzers and the purity decays from 99% to 97% within a matter of 3-4 days on normal scavenge.
We have to constantly flow new H2 gas to the unit to maintain good purity levels. What could be causing this issue?
thanks
Reply With Quote
  #2 (permalink)  
Old 05-31-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 10
Rep Power: 73
notevenclose is on a distinguished road
Default RE: DHCP H2 analyzers purity decay issue

Pressure too high? Im guessing with experience I have on a different hydrogen analyzer...
Reply With Quote
  #3 (permalink)  
Old 05-31-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 26
Rep Power: 81
dynasty is on a distinguished road
Default RE: DHCP H2 analyzers purity decay issue

I would start by checking your scavenge... try to increase it to see if it improves but monitor your bulk hydrogen usage. Then ensure your panel is oil and moisture free. sometimes there is the chance of seal oil entering into the analyzers. How is your dew points?
Reply With Quote
  #4 (permalink)  
Old 06-02-2008
PPF Member
Power Rookie
 
Join Date: Apr 2009
Posts: 14
Rep Power: 76
highvoltage is on a distinguished road
Default RE: DHCP H2 analyzers purity decay issue

thanks for the input.. turns out we had oil contamination in the DHCP tubing. We cleaned the piping and flow meters with nitrogen and verified our sealing system. Purity decay is no longer an issue. thanks
Reply With Quote
  #5 (permalink)  
Old 07-22-2009
PPF Member
Power Rookie
 
Join Date: Jun 2009
Posts: 13
Rep Power: 71
RedHawk is on a distinguished road
Thumbs up hydrogen panel

oil in the sensing lines is always an issue. question is where is it coming from? it is very costly to clean the tubes and even more so if the contamination has reached the cells. Oil in the hydrogen within the generator is typical but a substantial amount can lead to purity decay. True, a high flow scavange can band-aid the issue but you need to look into the oil/hydrogen seal system. do you have proper differential pressure, are the clearances acceptable on the shaft to seals diaphragms? What is the vacuum and are your drain enlargements doing their thing?
I have head of users placing a filtration system upstream of the inlet sensing line but this is only masking a true problem.
Reply With Quote
Reply

Bookmarks

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Subscribe to Power Plant Forum

All times are GMT -4. The time now is 12:04 PM.
Powered by vBulletin® Version 3.8.2
Copyright ©2000 - 2012, Jelsoft Enterprises Ltd.
Search Engine Friendly URLs by vBSEO 3.3.0