we inspect the grounding and excitation brushes once weekly, we change it according to its thickness, and we change the excitation brushes at base load (up to 250 MW) but with one brush at time, if we removed two brushes at the same time the generator will trip.

siemens generator (50 Hz - 16.5 KV)
Excitation voltage = 255 VDC