Originally Posted by Tony View Post
Chrisd,
Do you actually run the unit up to rated 110% speed to test the overspeed? How do you test the electrical check and the mechanical bolt? Is the mechanical bolt set at the same pickup as the electrical check?
thanks
We first run up to OPC, which takes control of the governer valves and shuts the Reheat stop valves at 103%. We then electrically disable this feature and run up to 108% electrical trip setpoint. After that, we'll disable (via logic point force) the electrical trip and run up to 110% for the mechanical overspeed verification. During all this testing, we verify with a reed tach locally as well as indicated on DCS. Vibration monitoring is also crucial. There is a complete approved procedure we follow, it also states that we must be online at min. 10% load for 4 hours prior to testing. These are completed annually, usually post-overhaul.